Forgive me - first timer here, but I'm striking out on Google searches.
I live in a condo with central venting for the bathrooms & kitchen. The microwave is installed above the stove and hooks into said system. There's an AC current switch (model EC-1420N) leading to what I believe is a step down transformer (no distinguishing model or make listed) that then feeds a Honeywell damper Operator (model M847D1004)e outlet power feeds the AC switch with hot to L1 and the neutral runs through hole in the switch.
T1 off the switch feeds the transformer which I assume steps down voltage & watts as the damper switch is rated at 24VAC, 60Hz, 6W.
Something is not functioning, as the damper is not opening when I turn on the fan so no air is actually leaving my domicile.
I'm was getting 1 amp of current through the center of the switch, so I stripped back more wire & looped it again to get 2 amps. Still nothing.
The odd thing is, with the vent off or on, I'm measuring 120v off both leads of the AC switch. Meaning it's always closed & always sending power to the (what I assume) transformer, then to the damper switch.
I tried disconnecting the lead going to the transformer, but that didn't do anything either.
The wires from the transformer to the damper switch measure 10ths of amps, so not enough to power it.
Pictures here: https://i.stack.imgur.com/XQMNx.jpg
looped it again to get 2 amps... why would you think that making a loop in the wire would increase the current? – jsotola Mar 30 '21 at 06:45