14

One time at my job we had some electrical work that needed done. The electrician had a small homemade switch box with a 120v mains plug running out of it and a switch on the front. The device basically threw whatever breaker that plug was attached to so he new which one needed work on and made the circuit safe. Where can I get one of those boxes, or a way I can trip the breaker from the outlet?

Daniel Griscom
  • 6,269
  • 33
  • 31
  • 41
Brent1409
  • 143
  • 1
  • 1
  • 6
  • Just as an aside, while it's not really possible or practical to test circuit breakers in situ it is possible to test RCDs using specialist equipment. This isn't done for identification purposes, however, but rather for testing and verification. – Dan Dec 30 '16 at 16:25
  • 4
    Is there a safe way you can trip a breaker from the outlet? No. What are you actually trying to do? – Mazura Dec 30 '16 at 22:30
  • Thanks everyone for your insite. It looks I'm just going to have to turn off the main switch and swap out these outlets. The guy that had this device wasn't the one that wired my house, but they are cut from the same cloth. I don't have much knowledge in house wiring so I wanted to ask before doing something stupid. I'm glad everyone pointed out its dangerous. I do have a Fluke tone generator/probe for cat5 so I suppose I could use that to trace the wire. – Brent1409 Jan 05 '17 at 05:17

7 Answers7

53

That box should have been a warning that the guy was incompetent; it's a very bad idea. If the breaker malfunctions, it can start a house fire.

There are cheap devices available in most home centers and hardware stores which can put a signal onto the wire and pick that up at the breaker to identify which breaker controls that outlet. There's a better version that a pro should have which can do a few other things.

Or there is the traditional homeowner solution: plug a radio into the outlet, turn up the volume so you can hear it from the basement, and try breakers until you find the one which silences the radio.

keshlam
  • 28,994
  • 5
  • 48
  • 98
  • 8
    Also, once you have found the correct breaker, write it down somewhere, preferably close to the breakers. – SQB Dec 30 '16 at 14:18
  • 6
    You could make a device with a suitable resistor and fuse greater than the breaker which would be reasonably safe. But I agree with your conclusion. – Chris H Dec 30 '16 at 18:56
  • @SQB Preferably on label stickers beside the switch itself. – jpmc26 Dec 31 '16 at 21:32
  • 2
    I think this answer would be better if it included a guess as to how the box worked and details on why it is unsafe. It mentions starting a fire but doesn't explain how or why that would happen. I don't know the OP's intent but it seems like that would make this answer complete. – D. Patrick Jan 01 '17 at 00:25
  • 1
    @D.Patrick: It is not something I want to encourage people to try. I cited the right answers. Use them. – keshlam Jan 01 '17 at 06:58
  • 1
    I don't mean encourage people to try it. I mean answer the question. "The box probably shorts the circuit. At best there is resistive load and this is moderately dangerous. At worst there is no resistive load and this is very dangerous. That's because with a load, the draw should trip the breaker before the components have time to heat. Without it they'll heat before the breaker trips. If the breaker doesn't work, both could cause a fire. You could not purchase something like this commercially. Here are some safer alternatives:". Or something like that with technical accuracy. – D. Patrick Jan 01 '17 at 12:34
  • On another note, I like the homeowner solution. I use an iPhone and an iPad and FaceTime myself so I can see the lights go out. – D. Patrick Jan 01 '17 at 12:37
  • The radio technique is dangerous because it suggests you are working on electric circuits without another mobile and vocal human in your house (Someone who could call out when a lamp went out, for example.) The most important safety equipment for an amateur electrician is a mobile and vocal human to call 911 for them when things go wrong. – Kate Gregory Jan 01 '17 at 13:29
  • 5
    @kategregory, we will have to agree to strongly disagree on that one. Yes, working alone can be dangerous, but that's true of almost any task from gardening to cooking to you-name-it. The better solution is to work properly so things don't go wrong in the first place. House current can be dangerous, but following fairly basic rules does manage the risk for simple tasks to an acceptable level. And part of what we're here for is to answer questions about how to do so. – keshlam Jan 01 '17 at 14:41
  • 1
    @KateGregory: If flipping breakers can get you electrocuted, you're already way past the point where it's safe to do any electrical work with your house, regardless of how many people you have with you. – Vikki Jan 23 '21 at 23:48
24

The answer which states that this is a bad idea is correct.

To answer your actual question: you could build such a device in about five minutes. Take an extension cord, cut it in half, attach the white and black wires to an ordinary light switch, and wrap the whole thing in a handy box.

When plugged in and the switch is closed, a short circuit is created that will either trip the breaker if it is working, or start a fire inside the walls if it is not.

Mazura
  • 13,377
  • 1
  • 18
  • 56
Eric Lippert
  • 1,310
  • 9
  • 13
  • 10
    While you answered the question, I downvoted because you didn't but in big bold text, "THIS IS A TERRIBLE IDEA AND YOU RUN A HIGH RISK OF DAMAGING BREAKERS AND POTENTIALLY BURNING DOWN YOUR HOUSE" – Aloysius Defenestrate Dec 30 '16 at 17:08
  • 1
    @AloysiusDefenestrate My suggested edit as per http://meta.diy.stackexchange.com/a/661/21695 was rejected. – Andrew Leach Dec 30 '16 at 17:13
  • 9
    The answer clearly states that this is a bad idea and what the consequences are. I invite both of you to write your own answers that you like better. – Eric Lippert Dec 30 '16 at 17:14
  • 1
    Plus one. OP asked for "a way I can trip the breaker from the outlet". TL;DR: short it out. They never asked if they should. The other half of the question is asking where to get something that's homemade... - @AloysiusDefenestrate - that comment belongs on the question. – Mazura Dec 30 '16 at 22:23
  • 1
    I’d like to further point out that this is done by people, and the part that is damaged is where contact is made (the switch), so you don’t just jump the circuit directly but connect leads to it first and then damage the other ends of those leads. – JDługosz Dec 31 '16 at 07:39
  • So stating it is a BAD IDEA makes it OK to suggest that one take a pair of needle-nose pliers or even a couple inches of wire stripped out of some romex and short the hot and neutral as a simple way of testing a breaker trip? It should be noted also that tripping breakers on various brands does shorten the breakers useful life. – spicetraders Dec 31 '16 at 14:21
  • 1
    @spicetraders: No one is suggesting that; saying that something is a bad idea that can burn your house down is the opposite of suggesting it. – Eric Lippert Dec 31 '16 at 14:51
  • 1
    @Eric Lippert In todays world there are many who skip the words BAD IDEA and will build the item and use it (from OP at least one so called electrician already has). Your post for example fails to mention what type of electrical extension cord, many have 14,16, or 18 gauge wire int them. On a 20A outlet what will fry and flame first the extension cord held in the operators hand or the breaker. If you post a bad idea you should greatly emphasize the details to attempt identify how and why to build it as safe as possible more then a simple answer. As some one will build it as you describe. – spicetraders Dec 31 '16 at 17:44
  • 1
    @spicetraders: Awesome. I invite you to write an answer which does just that! – Eric Lippert Dec 31 '16 at 17:48
  • @EricLippert I would not as there is no safe answer for shorting out a outlet. The answer is dangerous. – spicetraders Dec 31 '16 at 17:53
  • 1
    @spicetraders: That's correct. Which is why I said it was a bad idea that could burn your house down. Your comments say that I should both describe how to build this device safely, and not describe how to build this device safely, so I am at a loss to understand what it is you would prefer I do. What I would prefer you do is write your own answer that you like better, if you don't like this one. – Eric Lippert Dec 31 '16 at 18:15
  • 12
    I'm with Eric on this one. Stack exchange is polluted with answers that just say "don't." Sometimes I am looking for a bad idea. Not because I want to do it but because I want to understand how it works and why it is bad. By all means say "this is wrong," but at least answer the question. This answer didn't deserve a down vote. I don't think it is the best answer but I'm gonna upvote it so we don't punish answerers who answer the actual question asked. Also, @EricLippert, funny to run into you outside of stack overflow. – D. Patrick Jan 01 '17 at 00:21
  • 2
    @D.Patrick - "Sometimes I am looking for a bad idea." +1. I, myself, of course, have never made an outlet-popper... I mean um, a thingamajig whatchamacallit thingy. If you are going to use one; use your foot. You don't want your face anywhere near it. (This is if you have to ask territory. DVs should be directed at the question.) – Mazura Jan 04 '17 at 04:50
  • 2
    @EricLippert Thanks for the answer. Even when something is wrong there is still value in knowing why its wrong. You learn something besides being told what a dolt your electrician was and to check the label. I know something's wrong, but I'm not going to go sticking a rigged contraption up. – Brent1409 Jan 05 '17 at 05:25
18

That box works by connecting the live and neutral wires of the circuit to each other, i.e. it makes a short-circuit.
If all goes well, the fuse trips/blows. But as @keshlam said, it's a dangerous way to make a breaker trip: you're overloading the circuit. I did this once by accident, and had a 10 cm long flame blast out of the breaker box as the fuse tripped. Not the kind of thing you want to do on a regular basis.

Hobbes
  • 582
  • 2
  • 11
  • 9
    Exactly - it's kind of like testing your fire proofing by starting a fire. While things shouldn't go wrong if all is well, if all is not well there are multitude of possibilities - you could take out the main incoming fuse, the main circuit breaker (if applicable), an unknown fuse between (For example, some plugs in kitchens might be on a fused spur) among other things or maybe just start a good old fashioned fire. For the love of god, do NOT do this stuff deliberately. – Dan Dec 30 '16 at 16:29
  • 5
    Not to mention the extension cord could melt in your hands. – Dave Dec 30 '16 at 16:00
  • 1
    Guys doing electrical work in our highschool did this. Put multimeter probes in each outlet, waited until the breaker tripped, and moved on to the next outlet (there was single breaker per outlet). – Cysioland Dec 30 '16 at 19:35
  • 5
    @Dan: In some cases there could be value in applying a moderate overload which should trip any properly-functioning breaker within a second, and ensuring that whether or not the breaker trips the overload won't last more than a few seconds. An overload which is small enough that a UL-approved breaker could take a second to trip shouldn't cause dangerous overheating in less than five. If things are wired correctly, stress-testing shouldn't be necessary, but if e.g. there's a connection between the hots coming out of two breakers, such a fault might allow part of a circuit to draw... – supercat Dec 30 '16 at 21:57
  • 3
    ...twice as much current as it should without tripping a breaker or worse--it could allow part of a circuit to draw four times the rated current while a breaker took as long to trip as it would for a 2x overload. Since a 4x overload would heat the wire four times as much as a 2x overload, that could easily get into dangerous territory. – supercat Dec 30 '16 at 22:00
  • @Cysioland Those guys are idiots. The probes are not rated for 15A. If they came across a bad breaker, they just set the multimeter on fire, possibly electrocuted themselves and/or burned the place down. – Nelson Jul 25 '23 at 07:44
9

The reason this isn't completely deranged at that industrial location is that certain industrial sites follow slightly more permissive rules owing to having on-site electricians with scheduled, proactive maintenance. You see this phraseology in certain NEC rules. Their work is done to a higher caliber than home wiring; THHN in metal conduit, no backstabs on the premises, frequent inspections, most circuits meggered, etc.

Doing this in a residential location with lax residential rules and work of unknown provenance is suicide.

Obviously the switch is basically dead-shorting the hot and neutral to induce a trip, but if you do that in a residence, you have about a 50/50 chance of inducing future arc faults at a backstab, or at the least, fusing it open. We get lots and lots of "plugged in a (well within legal range) large load and a backstab failed" questions. You also have a chance of other stupidity, like discovering why FPE and Zinsco panels are panela nongrata.

Harper - Reinstate Monica
  • 300,628
  • 26
  • 286
  • 734
2

The safe answer to this would be to have an electrician install remote controlled circuit breakers, with a suitable trip circuit installed at the outlet where you want to remotely trip the breaker. (Eaton says they come in a CLR form factor for residential panels.)

Of course, properly labeling the panel, perhaps with a map showing where outlets/lights for each circuit would be a much cheaper and easier solution, and arguably more useful.

enter image description here

Johnny
  • 4,855
  • 9
  • 28
  • 36
0

Let's assume the guy with the box was not incompetent or insane and that he had actually devised a reasonably safe means to do this. What would it take? Below, I present a design that should work. I want to emphasize that I have not built this or tested it - this is purely theoretical. If you want to try it, do so at your own risk. I understand the fact that commercially available devices are out there that can identify circuits. Nonetheless, I have often wanted something similar to what was requested here, and the interest in this post tells me I am not alone. So here are my thoughts.

First of all, a couple of electronic principles. Ohms law states that Voltage (V) is the product of Current (I) and Resistance (R), V = I x R. A typical home circuit is supposed to be 120V. The standard circuit breaker is rated for 15 Amps. Using Ohms law, we can rearrange the equation as follows: R = V / I. So, 8 = 120 / 15. This means that an 8 Ohm load would draw 15 amps at 120 Volts. Resistance less that 8 Ohms would draw more than 15 Amps, and should trip the breaker.

Now, don't go out and buy an 8 Ohm resistor from radio shack and hook it up just yet. The other factor we need to consider is power dissipation. Power (Watts) is the product of voltage (Volts) and current (Amperes), Watts = Volts x Amperes. So, at full load, a 120 V, 15 Amp circuit provides up to 1800 Watts of power. This means that, with 8 Ohms of resistance and 120 Volts, the box would need to be capable is dissipating 1800 Watts. The resistors you see on circuit boards are typically something like 0.25 Watts. That won't work.

What we need now is a resistive element capable of dissipating the power. A simple method would be to create a box that has multiple screw-based light bulbs, and to get some high wattage bulbs, and have enough of them connected to exceed 1800 Watts. You could add toggle switches for each bulb, and then switch on one at a time until the current draw was too high and the breaker tripped. The advantage here is that you would be dealing with components normally designed to be powered by 120V, and all the wiring and switching would be standard stuff. The problem is that such a box would be bulky and it is getting harder to find high wattage bulbs. Plus, light bulbs break.

An alternative would be to use wire-wound power resistors. For about $18 each, you can buy power resistors capable of dissipating 300 Watts each. Power is additive, so if we have at least 6 resistors, we could handle 1800 Watts. That being said, it is not a good idea to run things at their limit. So I would design a circuit with at least 8 such resistors, so it could handle 2400 Watts, a reasonable safety factor. Home voltage is often as high as 125 Volts, and the breaker might allow more than 15 Amps to flow before tripping; 2400 Watts gives a safety factor of 33%, so we should be OK.

These resistors come in various values. A 16 Ohm, 300 Watt power resistor would be my choice. Back to basic electronics. In a series circuit, Resistance of the Total circuit (RT) is the sum of each individual resistance: RT = R1 + R2 + ... + Rn. In a parallel circuit, Resistance of the Total circuit (RT) with multiple resistors in parallel (R1, R2, etc.) is calculated by the following equation: 1 / RT = (1 / R1) + (1 / R2) + ... + (1 / Rn). Putting two 16 Ohm resistors in series makes a 32 Ohm resistor. Placing four 32 Ohm resistances in parallel makes a total resistance of 8 Ohms. That should draw 15 Amps and may or may not trip the circuit. Adding a fifth 32 Ohm pathway in parallel makes a total resistance of 6.4 Ohms, which would draw over 18 Amps and should trip the circuit.

So the idea would be to make a box, with a switch for each pathway, that has at least 5 32-Ohm pathways, each capable of dissipating 600 Watts. Switching on the first 4 would draw about 15 Amps from 120 V, switching on the fifth would go over 18 Amps and should trip the breaker. If you wanted to add a sixth, you could also potentially trip a 20 Amp circuit.

Here is a diagram with five pathways.

The resistors would cost you something like $120. The light switches could be standard stuff. You would need to make sure to wire it with wire capable of carrying enough current. Each 32 Ohm pathway would carry 3.75 Amps. Heavy gauge lamp cord would do the trick.

enter image description here

  • 2
    Breakers don't immediately break above their rating. 18A will trip the breaker thermally after 1000s or 17min. That's impractical. To trip within 1s magnetically you need to draw 300A, and that's dangerous. For trip charts see https://diy.stackexchange.com/questions/200353/can-i-run-a-15a-table-saw-on-a-15a-circuit-if-there-are-also-shop-lights-on-the – P2000 Apr 06 '21 at 14:59
  • 2
    OK - thank you for explaining. Seems like there really is no good way to do this. I should have checked the performance characteristics of the breaker. Very interesting - thank you for helping me understand. – John Buford Apr 06 '21 at 19:56
-1

Tripping a breaker by creating a short this way is unsafe. Please do not do it.*

There is however a use for such device (without or without a switch):
When you are working on a circuit, and you are not the only soul within a mile, you put the device into known outlet on same circuit. A thick bare wire jammed into socket works too. You do this after identifying which breaker controls which sockets and turning the breaker off.
This way, if some dumbass comes along and decides "oh, breaker dropped, lets turn it on!", you will hear it, they get a firework show, and you (probably) only get a short jolt. Better safe than sorry. My electrician had this happen to him. I personally wire tie the breakers when working on things or put a short wire in socket since then.
Just remember to remove it afterwards.

(*) There is also an emergency use - if someone on the circuit is being electrocuted, or things are on fire, and no safety worked, you do whatever to trip that circuit.